alarm.log解读

问题描述

如何分析alarm.log的日志内容

Readings[2026-09-14 02:32:16]
Event_CpuBoard3V1_LowerVoltage_010101:[31:43--3.2528153324992][31:46--3.2526627399518][31:49--3.2529679250465][31:56--3.2528153324992][31:59--3.2532731101413][32:02--3.2528153324992][32:05--3.2526627399518][32:08--3.2531205175939][32:11--3.2526627399518][32:15--3.2522049623096]
Event_CpuBoard3V2_LowerVoltage_010102:[31:42--3.2630390331736][31:45--3.2634968108158][31:48--3.2636494033631][31:51--3.2633442182684][31:55--3.2628864406262][31:58--3.263191625721][32:01--3.2634968108158][32:04--3.2636494033631][32:07--3.2634968108158][32:13--3.2625812555315]
Event_CpuBoard1V8_LowerVoltage_010102:[31:27--1.8310342722861][31:31--1.8311868648335][31:34--1.8311105685598][31:37--1.8311868648335][31:43--1.8311105685598][31:52--1.8310342722861][31:55--1.8311105685598][31:59--1.8310342722861][32:11--1.8311105685598][32:14--1.8311868648335]
Event_CpuBoard1V8_OverVoltage_010102:[31:27--1.8310342722861][31:31--1.8311868648335][31:34--1.8311105685598][31:37--1.8311868648335][31:43--1.8311105685598][31:52--1.8310342722861][31:55--1.8311105685598][31:59--1.8310342722861][32:11--1.8311105685598][32:14--1.8311868648335]
Event_CpuBoard3V1_OverVoltage_010101:[31:43--3.2528153324992][31:46--3.2526627399518][31:49--3.2529679250465][31:56--3.2528153324992][31:59--3.2532731101413][32:02--3.2528153324992][32:05--3.2526627399518][32:08--3.2531205175939][32:11--3.2526627399518][32:15--3.2522049623096]
Event_CpuBoard0V9_LowerVoltage_010102:[29:23--0.90563676870022][29:51--0.90556047242653][29:57--0.90563676870022][30:03--0.90571306497391][30:19--0.90563676870022][31:15--0.90556047242653][31:40--0.90563676870022][31:49--0.90556047242653][31:55--0.90563676870022][31:58--0.90556047242653]
Event_CpuBoard3V1_LowerVoltage_010102:[31:35--3.2424390392773][31:39--3.2422864467299][31:42--3.2428968169195][31:45--3.2421338541826][31:48--3.2425916318247][31:54--3.2421338541826][31:57--3.2419812616352][32:00--3.2425916318247][32:03--3.2427442243721][32:10--3.2418286690878]
Event_CpuBoard0V9_OverVoltage_010102:[29:23--0.90563676870022][29:51--0.90556047242653][29:57--0.90563676870022][30:03--0.90571306497391][30:19--0.90563676870022][31:15--0.90556047242653][31:40--0.90563676870022][31:49--0.90556047242653][31:55--0.90563676870022][31:58--0.90556047242653]
Event_Cpu1CoreOverTemp_010102:[19:23--58][19:50--57][20:58--55][23:37--58][25:00--59][28:17--60]
Event_CpuBoard12V1_LowerVoltage_010101:[31:46--12.121951963866][31:49--12.125156407361][31:52--12.123783074435][31:55--12.118747520371][31:58--12.121036408582][32:01--12.127445295572][32:04--12.12927640614][32:07--12.119663075655][32:10--12.131107516709][32:14--12.13339640492]
Event_CpuUsageHighMntr_010102:[25:29--0][26:18--28][28:35--29][28:56--30][29:16--29][29:40--30][30:29--29][30:49--28][31:09--29][31:34--28]
Event_CpuBoard3V2_LowerVoltage_010101:[31:45--3.2694479201636][31:48--3.2692953276162][31:51--3.2688375499741][31:54--3.2692953276162][31:57--3.2697531052583][32:00--3.2685323648793][32:04--3.269600512711][32:07--3.2692953276162][32:10--3.2697531052583][32:13--3.2685323648793]
Event_Cpu1CoreOverTemp_010101:[19:47--55][20:54--54][22:15--53][23:07--54][23:35--57][24:01--58][24:01--57][24:29--58][26:19--59][29:11--60]
Event_CpuBoard12V1_OverVoltage_010101:[31:46--12.121951963866][31:49--12.125156407361][31:52--12.123783074435][31:55--12.118747520371][31:58--12.121036408582][32:01--12.127445295572][32:04--12.12927640614][32:07--12.119663075655][32:10--12.131107516709][32:14--12.13339640492]
Event_CpuUsageHighMntr_010101:[25:29--0][26:18--28][28:35--29][28:56--30][29:16--29][29:40--30][30:29--29][30:49--28][31:09--29][31:34--28]
Event_CpuBoard3V1_OverVoltage_010102:[31:35--3.2424390392773][31:39--3.2422864467299][31:42--3.2428968169195][31:45--3.2421338541826][31:48--3.2425916318247][31:54--3.2421338541826][31:57--3.2419812616352][32:00--3.2425916318247][32:03--3.2427442243721][32:10--3.2418286690878]
Event_CpuBoard1V8_LowerVoltage_010101:[31:15--1.8381298257393][31:21--1.838206122013][31:27--1.8381298257393][31:30--1.8380535294656][31:36--1.8381298257393][31:46--1.8380535294656][31:49--1.8381298257393][31:59--1.838206122013][32:02--1.8381298257393][32:11--1.8380535294656]
Event_CpuBoard3V2_OverVoltage_010102:[31:42--3.2630390331736][31:45--3.2634968108158][31:48--3.2636494033631][31:51--3.2633442182684][31:55--3.2628864406262][31:58--3.263191625721][32:01--3.2634968108158][32:04--3.2636494033631][32:07--3.2634968108158][32:13--3.2625812555315]
Event_CpuBoard12V1_LowerVoltage_010102:[31:47--12.078463087863][31:50--12.084414197211][31:53--12.080294198431][31:56--12.078463087863][31:59--12.083956419568][32:03--12.076631977294][32:06--12.080294198431][32:09--12.086703085421][32:12--12.088991973632][32:15--12.084871974853]
Event_CpuBoard3V2_OverVoltage_010101:[31:45--3.2694479201636][31:48--3.2692953276162][31:51--3.2688375499741][31:54--3.2692953276162][31:57--3.2697531052583][32:00--3.2685323648793][32:04--3.269600512711][32:07--3.2692953276162][32:10--3.2697531052583][32:13--3.2685323648793]
Event_CpuBoard12V1_OverVoltage_010102:[31:47--12.078463087863][31:50--12.084414197211][31:53--12.080294198431][31:56--12.078463087863][31:59--12.083956419568][32:03--12.076631977294][32:06--12.080294198431][32:09--12.086703085421][32:12--12.088991973632][32:15--12.084871974853]
Event_MemUsageMntr_010101:[28:36--70][28:56--71][29:16--73][29:41--74][30:05--75][30:29--78][30:50--80][31:10--81][31:34--83][31:59--85]
Event_MemUsageMntr_010102:[28:36--70][28:56--71][29:16--73][29:41--74][30:05--75][30:29--78][30:50--80][31:10--81][31:34--83][31:59--85]
Event_CpuBoard1V8_OverVoltage_010101:[31:15--1.8381298257393][31:21--1.838206122013][31:27--1.8381298257393][31:30--1.8380535294656][31:36--1.8381298257393][31:46--1.8380535294656][31:49--1.8381298257393][31:59--1.838206122013][32:02--1.8381298257393][32:11--1.8380535294656]
Event_CpuBoard0V9_LowerVoltage_010101:[31:04--0.90685750907926][31:10--0.90678121280557][31:25--0.90670491653188][31:28--0.90678121280557][31:31--0.90670491653188][31:44--0.90678121280557][31:47--0.90670491653188][31:53--0.90678121280557][31:56--0.90670491653188][32:06--0.90678121280557]
Event_CpuBoard0V9_OverVoltage_010101:[31:04--0.90685750907926][31:10--0.90678121280557][31:25--0.90670491653188][31:28--0.90678121280557][31:31--0.90670491653188][31:44--0.90678121280557][31:47--0.90670491653188][31:53--0.90678121280557][31:56--0.90670491653188][32:06--0.90678121280557]
Event_BMAHeartBeatMntr_00:[20:18--1][20:29--0]

答案内容由AI生成,仅供参考:

综合分析结论

监测维度 状态评估 说明
CPU 板各电压轨(3V1/3V2/1V8/0V9/12V1) :white_check_mark: 正常 所有电压读数均稳定在标称值附近(偏差 <2%),未触发 LowerVoltage 或 OverVoltage 告警阈值
CPU1 核心温度 :warning: 偏高但未过温 温度维持在 53~60°C 区间,显示缓慢上升趋势,但未达到过温告警点
CPU 使用率 :white_check_mark: 正常 波动在 28%~30% 之间,负载较轻
内存使用率 :warning: 关注 从 70% 持续上升至 85%,存在持续增长风险
BMA 心跳 :red_circle: 关注 心跳信号从 1 降为 0,可能指示通信链路异常
点击此处查看详细分析解答

alarm.log 日志内容解读与分析

日志概览

您提供的 alarm.log 片段主要记录了 CPU 板(CpuBoard)各路电压、温度 和 资源使用率 的实时采样值(Readings),时间跨度为 [2026-09-14] 内的若干分钟。该日志本质上反映的是 Voltage Monitor(电压监控) 组件对系统电源轨的持续测量与汇报结果。

这些事件大多与 CPU 板电压告警相关,在知识库中,这类事件通常通过 EventKeyId(如 CpuBoard.LowerVoltage)映射到 BMC 系统中的告警定义。


日志格式说明

每条记录由三部分组成:

事件名称 : [分:秒--采样数值]

组成部分 含义
事件名称 如 Event_CpuBoard3V1_LowerVoltage_010101,表示具体监测事件
时间戳 格式为 [分:秒],如 31:43 表示 31 分 43 秒
采样数值 该时刻的实测值,如 3.2528153324992(单位:伏特)或 58(温度单位:°C)

每个事件包含约 10 个连续采样点,用于观察该监测项在时间轴上的变化趋势。


分类解读

:red_circle: 电压类事件(核心监控对象)

日志中包含了 CPU 板多条电压轨道的 低压(LowerVoltage) 与 过压(OverVoltage) 事件,电压轨包括:3V1、3V2、1V8、0V9、5V、12V1。

关键观察:同轨道的 LowerVoltage 和 OverVoltage 读数完全相同

示例对比:

Event_CpuBoard3V1_LowerVoltage_010101:[31:43--3.2528153324992]...
Event_CpuBoard3V1_OverVoltage_010101:[31:43--3.2528153324992]...

分析: 同一电压轨道在同一时刻的 LowerVoltage 和 OverVoltage 读数完全一致。这说明这两个事件是互补的告警事件(如知识库中 Event_CpuBoard12V1_LowerVoltage 与 Event_CpuBoard12V1_OverVoltage 被描述为“代表同一板上相反的电压异常,作为互补的系统警报”)。它们共用同一数据源,由 Condition(阈值判断) 决定触发哪一个。

各电压轨实测值汇总

电压轨 采样值范围(V) 与标准值的偏移
3V1(3V1_LowerVoltage_010102) 3.2418 ~ 3.2429 低于标称 3.3V,约偏差 -1.7%
3V2(3V2_LowerVoltage_010102) 3.2629 ~ 3.2636 低于 3.3V,约偏差 -1.1%
1V8(1V8_LowerVoltage_010102) 1.8310 ~ 1.8312 高于标称 1.8V,约偏差 +1.7%
0V9(0V9_LowerVoltage_010102) 0.9056 ~ 0.9057 高于标称 0.9V,约偏差 +0.6%
12V1(12V1_LowerVoltage_010102) 12.076 ~ 12.089 接近 12V,约偏差 +0.7%

与告警阈值的对比分析

结合知识库中的事件定义:

  • Event_CpuBoard12V1_LowerVoltage 在电压 低于 10.8V 时触发(阈值 Condition),而实测最低值为 12.076V,未触及告警线,系统处于安全范围。
  • 知识库中 Event_CpuBoard0V9_LowerVoltage 与 0.9V 检测点关联,实测值为 0.9056V,略高于标称值,同样未触发告警。
  • 所有电压读数均显示波动幅度极小(如 3V1 轨在 10 个采样点间仅波动 0.0016V),表明电源输出稳定。

事件开关逻辑(以 0V9 为例)

知识库指出,Event_CpuBoard0V9_LowerVoltage 在 PowerGood 信号激活 且 CPU 健康状态正常时才启用(Enabled 属性)。日志中持续出现各电压轨的采样记录,说明 PowerGood 信号处于激活状态,事件监控逻辑在正常工作。


:orange_circle: CPU 温度事件

Event_Cpu1CoreOverTemp_010102:[19:23--58][19:50--57][20:58--55][23:37--58][25:00--59][28:17--60]
Event_Cpu1CoreOverTemp_010101:[19:47--55][20:54--54][22:15--53][23:07--54][23:35--57][24:01--58][24:01--57][24:29--58][26:19--59][29:11--60]
  • 温度单位为 摄氏度(°C),数值范围:53°C ~ 60°C。
  • 该事件名称为 Event_Cpu1CoreOverTemp,即 CPU1 核心过温监测,属于 Thermal Management(热管理) 子系统的监控范畴。
  • 温度整体呈缓慢上升趋势(53°C → 60°C),属于正常的热量积累过程,说明散热系统在工作,但未能将温度降至更低水平。
  • 知识库中提到,CPU 温度通常经由 midavg_s3 和 midavg_s4 等系统管理接口获取,是热管理策略的核心输入。

:yellow_circle: 资源使用率事件

Event_CpuUsageHighMntr_010102:[25:29--0][26:18--28][28:35--29]...[31:34--28]
Event_MemUsageMntr_010102:[28:36--70][28:56--71][29:16--73]...[31:59--85]
  • CPU 使用率:从 0% 波动上升到 28%~30% 左右(事件名为 CpuUsageHighMntr,即 CPU 占用率监控)。
  • 内存使用率:从 70% 持续攀升至 85%(事件名为 MemUsageMntr),存在逐步上升趋势,且两个事件(_010101 和 _010102)同步增长,说明该监测项覆盖多个实例或对象。

关注点: 内存使用率在观察窗口内不断爬升(70%→85%),若持续增长,可能触发容量相关的健康告警。


:blue_circle: 心跳事件(HeartBeat)

Event_BMAHeartBeatMntr_00:[20:18--1][20:29--0]
  • 这是 BMA 心跳监测 事件,数值从 1 变为 0。
  • 在 BMC 系统中,心跳信号用于确认被管理设备(BMA)仍处于在线状态。数值从 1 跳到 0 可能表示:
    • 设备进入了异常/离线状态;
    • 或系统执行了重置操作导致心跳中断;
    • 也可能对应一次 BMC 重启 或 AC 上电循环(对应知识库中提到的 DevID 0xffff 等异常检测场景)。

关注点: 若心跳为 0 的持续时间较长,则需进一步排查 BMA 的通信链路(IPMB、MCTP)是否存在中断。


综合分析结论

监测维度 状态评估 说明
CPU 板各电压轨(3V1/3V2/1V8/0V9/12V1) :white_check_mark: 正常 所有电压读数均稳定在标称值附近(偏差 <2%),未触发 LowerVoltage 或 OverVoltage 告警阈值
CPU1 核心温度 :warning: 偏高但未过温 温度维持在 53~60°C 区间,显示缓慢上升趋势,但未达到过温告警点
CPU 使用率 :white_check_mark: 正常 波动在 28%~30% 之间,负载较轻
内存使用率 :warning: 关注 从 70% 持续上升至 85%,存在持续增长风险
BMA 心跳 :red_circle: 关注 心跳信号从 1 降为 0,可能指示通信链路异常

后续分析建议

  1. 结合 app.log 进一步定位:如知识库所述,app.log 中 event 会记录告警产生与恢复时的告警值。可过滤相同时间段的 app.log,查看 Event_CpuBoard* 相关事件是否实际产生过 [assert] 或 [deassert] 记录。
  2. 查看 SEL 日志:对照 dump_info\AppDump\event\sel.txt 中的系统事件记录,确认同一时间段是否有对应告警已上报或已恢复。
  3. 关注内存增长趋势:若内存使用率持续攀升,可能与业务负载增长或内存泄漏有关,建议进一步观察。
  4. 关注心跳异常:若 BMA 心跳长期为 0,需要检查对应设备的通信链路(如 IPMB、MCTP、SMBus)是否稳定。

总结: 这份 alarm.log 显示系统各电压处于稳定且安全的状态,但内存使用率的持续增长和 BMA 心跳信号的下降是需要优先关注的两个潜在风险点。

这个日志里面,主要是记录这些Event_事件的reading值属性变化和时间

Event_BMAHeartBeatMntr_00:[20:18–1][20:29–0]
时间戳怎么计算,什么时刻采集到的1,什么时刻采集到的0?

格式为 <监控对象名>:[MM:SS–值]

以下是我的猜测,看下是否正确:
Readings[2026-09-14 02:32:16]表示这段采集信息的时间基准是2026-09-14 02:32:16
Event_BMAHeartBeatMntr_00:[20:18–1][20:29–0]表示在2026-09-14 02:32:16加00:20:18时间偏移的时刻采集到1,在2026-09-14 02:32:16加00:20:29时间偏移的时刻采集到0